Mike, you were right. I have never seen one trip but have toggled them many times.
Search found 995 matches
- Fri May 13, 2022 5:41 pm
- Forum: RADIAN Series
- Topic: In need of immediate help, Radian stopped working
- Replies: 22
- Views: 1059
- Fri May 13, 2022 4:42 pm
- Forum: RADIAN Series
- Topic: In need of immediate help, Radian stopped working
- Replies: 22
- Views: 1059
Re: In need of immediate help, Radian stopped working
The breakers will not go into the ON position, even with no power going to them. Since you are planning to replace the breakers. Take one of the breakers out of the system and see if it still won't go into the ON position. If it does we know there is something else going on. I would recommend that ...
- Fri May 13, 2022 2:43 pm
- Forum: RADIAN Series
- Topic: In need of immediate help, Radian stopped working
- Replies: 22
- Views: 1059
Re: In need of immediate help, Radian stopped working
There are two switches on the right side of the panel box on the Radian. I can get one to switch UP (on?), but the other will not. This behavior has alternated between those two switches. When the power first went out, both were in the UP position. I switched them off. Now only one at a time, and t...
- Fri May 13, 2022 11:24 am
- Forum: RADIAN Series
- Topic: In need of immediate help, Radian stopped working
- Replies: 22
- Views: 1059
Re: In need of immediate help, Radian stopped working
On your Mate3s, press the top left button and turn the inverter on. It is likely off.
- Wed May 04, 2022 3:55 pm
- Forum: SkyBox Inverter
- Topic: Over stringing
- Replies: 2
- Views: 840
Re: Over stringing
FWIW, I have not installed any Skyboxes. I think you are basing your concern on typical AC coupled inverters which have a specific ratio of panel power to inverter power that cannot be exceeded. The Skybox and other battery backed system take the PV power harvested with a MPPT Charge Controller (int...
- Wed May 04, 2022 3:42 pm
- Forum: OutBack
- Topic: heat pumps
- Replies: 6
- Views: 1431
Re: heat pumps
In our area I recommend mini-split heat pumps for my solar customers. For our 2,200 square foot log home we heat & cool with a 18,000 Btu/hr Mitsubishi mini-split. In winter we seldom get below 15°F at night and daytime temps are in the 35-45F range. The image below shows the performance data fo...
- Tue May 03, 2022 1:53 pm
- Forum: Off Grid Applications
- Topic: AGS run fault?
- Replies: 3
- Views: 46
Re: AGS run fault?
Since the generator ran for ~2 hours each time, I would suspect something with the generator voltage or frequency not being within parameters at that time. Do you have the input set to "generator?"
- Sat Apr 30, 2022 10:02 am
- Forum: Off Grid Applications
- Topic: What's the chassis ground/pe for?
- Replies: 4
- Views: 92
Re: What's the chassis ground/pe for?
Some comments: 1) Put white tape on your neutral to show it is the neutral. Black and Red are reserved for the hot legs. 2) Your Classic Lite 150 CC does not have a neutral. Neutral is only a function in the AC portion of the system. 3) The neutral and ground are to be only bonded (connected togethe...
- Wed Apr 20, 2022 3:54 pm
- Forum: Mate3 / Mate3s
- Topic: Unreliable Mate3 connection to the Internet
- Replies: 4
- Views: 85
Re: Unreliable Mate3 connection to the Internet
Have you updated the firmware on the Mate? Do you have a Mate 3 or Mate 3s? Most likely Mate 3s if bought in last 3-4 years.
- Thu Apr 14, 2022 4:26 pm
- Forum: Off Grid Applications
- Topic: Kohler 12RES Generator tripping (some) GFCI outlets
- Replies: 6
- Views: 83
Re: Kohler 12RES Generator tripping (some) GFCI outlets
On the 12-RES the N-G comes bonded from the factory and is located in the junction box on the generator.
- Fri Apr 08, 2022 12:41 pm
- Forum: OutBack
- Topic: Inverter monitoring facility
- Replies: 6
- Views: 1146
Re: Inverter monitoring facility
Go to this contact page https://outbackpower.com/opticsre-support-request and make the request. I am sure you will have to prove that previous owner sold it to you.
- Fri Apr 08, 2022 9:21 am
- Forum: FLEXnet DC
- Topic: Battery charge factor
- Replies: 3
- Views: 151
Re: Battery charge factor
Interesting technology for a 100+ year old battery chemistry:
Hoppecke Sun Air page - https://www.hoppecke.com/en/product/sun-air/
Hoppecke Sun Air manual - https://www.hoppecke.com/fileadmin/Reda ... ual_en.pdf
Hoppecke Sun Air page - https://www.hoppecke.com/en/product/sun-air/
Hoppecke Sun Air manual - https://www.hoppecke.com/fileadmin/Reda ... ual_en.pdf
- Mon Apr 04, 2022 1:12 pm
- Forum: Off Grid Applications
- Topic: Solar Panel Watts and Cost over last 25 years
- Replies: 9
- Views: 176
- Mon Apr 04, 2022 8:42 am
- Forum: Simpliphi
- Topic: SimpliPhi battery BMS
- Replies: 2
- Views: 125
Re: SimpliPhi battery BMS
It would be interesting to see a teardown of the BMS (raysun are you willing). A simple analog BMS could have a significantly longer life than a more complex digital IC BMS system.
- Mon Apr 04, 2022 8:33 am
- Forum: FLEXmax Charge Controllers
- Topic: RTS Function
- Replies: 2
- Views: 67
Re: RTS Function
If the RTS is working you will see the temp compensated voltage on the CC display and in OpticsRE on the inverter's status screen. On the CC do you have the Battery Temp Compensation Range set to Wide? If not change to Wide.
- Mon Apr 04, 2022 8:15 am
- Forum: Off Grid Applications
- Topic: Solar Panel Watts and Cost over last 25 years
- Replies: 9
- Views: 176
Solar Panel Watts and Cost over last 25 years
I recently upgraded the panels for a customer, who still had his receipts for his earlier panels. - 1995 288W for $1,916 or $6.65/watt - 2009 520W for $2,380 or $4.58/watt - 2022 1,170W for $1,053 or $0.90/watt As with many early adopters in 2nd home off-grid locations they were very frugal in their...
- Mon Apr 04, 2022 8:06 am
- Forum: Power System PV Combiner (PSPV)
- Topic: Question regarding PV grounding to combiner in attic
- Replies: 2
- Views: 129
Re: Question regarding PV grounding to combiner in attic
I would also recommend you look at the NEC. All DC PV wires need to be in EMT conduit and most likely in metal junction boxes. Logic is that if it an arc starts at that location the metal JB will contain it. Recommend you look at Soladeck for the roof penetration and also can be used for junction box.
- Tue Mar 29, 2022 6:22 pm
- Forum: FLEXmax Charge Controllers
- Topic: GFDI tripped
- Replies: 6
- Views: 141
Re: GFDI tripped
Highly unlikely it is the Midnite surge protectors. Are you able to see what the peak output amps were just prior to the trip, should be last entry in CC log? I recall on my personal system the GFDI tripping due to cloud edge effects causing momentary current spikes. Since I was not using my full FM...
- Thu Mar 24, 2022 8:46 am
- Forum: Mate3 / Mate3s
- Topic: Low battery voltage warning
- Replies: 16
- Views: 241
Re: Low battery voltage warning
Shut down the inverter and then start checking for loose connections on the batteries and at the inverter, including the connection between the GSLC and the inverter.
- Thu Mar 24, 2022 7:51 am
- Forum: Off Grid Applications
- Topic: Relays constantly failing
- Replies: 18
- Views: 462
Re: Relays constantly failing
Note from the tech sheet on it it's good for 32 amps at 30 VDC but drops way down to only 6 amps at 110 VDC. Reduced current at higher voltage is due to arcing. No arcing at low voltage, but at 80+ V you can create a significant arc with one string of PV panels supplying ~10A (FYI, speaking from ex...
- Sun Mar 20, 2022 9:49 am
- Forum: OutBack
- Topic: 60A circuit breaker letting 80A through?
- Replies: 20
- Views: 1051
Re: 60A circuit breaker letting 80A through?
'm actually talking about the conductors from the combiner box to the GLSC which are what that PV input breaker protects. We were "talking" about the same wire run. One way to visualize the issue is, assuming your panels could theoretically output 100A and you accidently shorted the two P...
- Sat Mar 19, 2022 9:47 am
- Forum: OutBack
- Topic: 60A circuit breaker letting 80A through?
- Replies: 20
- Views: 1051
Re: 60A circuit breaker letting 80A through?
Long story short, I downgraded from 80A to 60A breaker because 3 of the 4 strings use 6 gauge THWN-2 in conduit. Those conductors don't ever carry more than 60 amps but wouldn't be correct to have an 80A breaker on that circuit. The 4th string is in a different location so can't be combined with th...
- Sat Mar 19, 2022 7:54 am
- Forum: RADIAN Series
- Topic: Wire Sizes
- Replies: 11
- Views: 7243
- Sat Mar 19, 2022 7:54 am
- Forum: RADIAN Series
- Topic: Wire Sizes
- Replies: 11
- Views: 7243
Re: Wire Sizes
Most often we quote the ampacity of the wire based on it being in conduit along with the temperature rating of the wire. Often overlooked the temperature rating of the connections. For cabinet wiring (e.g., GSLC) one should use the NEC 2014 Table 310.15(B)(17) for free air, which allows for 6AWG: - ...
- Tue Mar 15, 2022 9:26 am
- Forum: OutBack
- Topic: FNDC - Battery Charging - Battery Ah calculation
- Replies: 3
- Views: 397
Re: FNDC - Battery Charging - Battery Ah calculation
Battery AH: is the C20AH capacity of the battery as specified by the manufacturer. The C20 AH rating is a good starting point and the one most of us use as it is typically published. The C20 AH battery rating is the capacity of the battery when discharged to a specified voltage in a 20-hour period ...