Re: Help needed reconfiguring system for LifePo4 batts

OK.

I'd suggest charging the two battery blocks separately to the same voltage, then recombining them.

Does there happen to be an ON/OFF switch on the battery blocks?
by raysun
Sat May 21, 2022 1:12 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

LiFePo4 cells are very low impedance (its why they need a BMS to act as "traffic cop"). Very minor differences in voltage make a very big difference in cell capacity. The leads need to be identical between the battery terminals and the battery bus bar (in your case the inverter battery ter...
by raysun
Sat May 21, 2022 12:43 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

How are the two connected? It would be best for each to be connected to discrete terminals on a battery bus bar using identical cables. Can you post photos of the battery connections? That being said, it is unusual for "downstream" blocks to be charging/discharging fastest. Some testing is...
by raysun
Sat May 21, 2022 9:54 am
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

Screenshot_20220521-064913_Firefox.jpg As you are making and tracking the results of changes to your system, you might find the Mate's internal web app useful. Access with any browser by entering the Mate's IP address (press the PORT key to find it). Its Read-Only so useful for monitoring. Since it...
by raysun
Sat May 21, 2022 8:43 am
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

GCC is not "Swiss Watch" precise. It will overshoot at times. However it hasn't been my experience that it automatically compensates for load. Then again, I only have my own system to go by.
by raysun
Fri May 20, 2022 8:07 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

Charge optimization tasks. FNDC Battery Charging Battery Ah: 200AH Charged Voltage: 27.8V Charged Time: 1 Minute Charged Return Amps: 6A Charge Factor: 97% I believe you may have already set these. This is my guess as to the best values for a typical Chinese LiFePo4. The main question will be the en...
by raysun
Fri May 20, 2022 5:12 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

Cheers!

And Aloha from Hawaii Island.
by raysun
Fri May 20, 2022 5:04 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

50A is a trivial increase as far as battery longevity is concerned. A good place to start. LiFePo4 charge fast. That's a great thing about them! If you can live with them for a while, the longer you have them in service, the better the battery choices when it comes time to replace them. There's no '...
by raysun
Fri May 20, 2022 4:27 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

There is one issue with loads , the inverter is not compensating for loads like it used to . PV input is currently 1.8kw , if I turn the toaster on which draws .9kw the PV input doesn’t go up to compensate for the load , the system draws from the batteries instead . Is the system off-grid? The batt...
by raysun
Fri May 20, 2022 4:11 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

The Mate3 I have does have global charge control…but it only works if grid tie is enabled , I have enabled it and set Max at input at 40A The grid-tie settings for GCC are a constant source of confusion. To clarify: • Global Charger Control requires Grid Tie Mode = Enabled on the FlexMax Charge Con...
by raysun
Fri May 20, 2022 1:15 am
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

Equipment list corrected ! Yes two blocks connected in parallel which is the maximum recommended and I have set charge current @ 20A but will change that . Put Batteries in today and switched system on just as sun was setting to be safe as I wasn’t 100% confident in my set points…turns out they are...
by raysun
Thu May 19, 2022 10:31 pm
Forum: Third-Party Batteries
Topic: Help needed reconfiguring system for LifePo4 batts
Replies: 21
Views: 131

Re: Help needed reconfiguring system for LifePo4 batts

Please check your profile and update the equipment list. A VFXR3048(E?) is listed, but its mentioned the system is 24V. How many of these 24V @ 100AH battery blocks are being planned? Does the BMS permit parallel connections? IMO, at least 2 blocks (24V @ 200AH) is a minimum. Looking at the specs, t...
by raysun
Thu May 19, 2022 11:43 am
Forum: Mate3 / Mate3s
Topic: Ethernet Addresses
Replies: 6
Views: 48

Re: Ethernet Addresses

The entries under Port look to be "legit" LAN addressing. Confirmed by being able to access the Mate using the IP address displayed. The entries under Ethernet Addresses would not work. Perhaps they were manually entered at some point? DHCP Enabled, so the Port addresses are likely configu...
by raysun
Wed May 18, 2022 9:35 pm
Forum: Simpliphi
Topic: Upgrading From FLAs to Simpliphi
Replies: 50
Views: 281

Re: Upgrading From FLAs to Simpliphi

Once done pushing buttons and the system settles down, I'd be curious if you're seeing battery charge event log entries akin to this:
Screenshot_20220518-183312_Firefox.jpg
by raysun
Wed May 18, 2022 9:21 pm
Forum: Simpliphi
Topic: Upgrading From FLAs to Simpliphi
Replies: 50
Views: 281

Re: Upgrading From FLAs to Simpliphi

For your battery, charge current is to be limited to 75 Amps. "Is this the case with two SimpliPhi batteries?" Yes I don't know about the Grid Tie Mode activity on the Mate3s, as I never had occasion to mess with it, except that the FX3048T isn't "grid interactive" so maybe the ...
by raysun
Wed May 18, 2022 7:43 pm
Forum: Simpliphi
Topic: Upgrading From FLAs to Simpliphi
Replies: 50
Views: 281

Re: Upgrading From FLAs to Simpliphi

I'm not 100% sure what sequence of configurations have occurred (but have an inkling.) For Global Charger Control, three parameters (and ONLY three parameters) are enabled: 20220518_163038.jpg FM80 Misc -> Grid Tie Mode = Enabled (Note its disabled here) 20220518_163111.jpg Mate3s Global Charge -> G...
by raysun
Wed May 18, 2022 6:43 pm
Forum: Mate3 / Mate3s
Topic: No PV or Inverter showing on Mate3s
Replies: 4
Views: 58

Re: No PV or Inverter showing on Mate3s

Check all the disconnects (circuit breakers) and make sure they are in the ON position. Were any wiring or configuration changes made recently? What type/brand/model battery? Looks like the battery has been charged (by solar?) and the FM80 is currently idle as it has nothing to do. Also, the inverte...
by raysun
Wed May 18, 2022 5:20 pm
Forum: RADIAN Series
Topic: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK
Replies: 8
Views: 381

Re: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK

I assume with such a small battery, run time is limited. Another consideration is the maximum charge current the battery will accept. AGMs have relatively low internal impedance, so accept a relatively high charge current, but there is a limit. A flooded lead acid battery may be limited to 10-15% of...
by raysun
Wed May 18, 2022 2:45 pm
Forum: Simpliphi
Topic: Upgrading From FLAs to Simpliphi
Replies: 50
Views: 281

Re: Upgrading From FLAs to Simpliphi

Disconnect PV, wait until FM shows idle (Snoozing, Sleeping, etc.), then reconnect PV to restart the FM80. Make sure you have Current Limit set to 75A. At 54.8V the battery is above Float voltage, so if the battery has been fully charged (check the Event Log), the FM has nothing to do at the moment....
by raysun
Wed May 18, 2022 2:01 pm
Forum: Simpliphi
Topic: Upgrading From FLAs to Simpliphi
Replies: 50
Views: 281

Re: Upgrading From FLAs to Simpliphi

GM raysun, not sure if a new topic is required however, my CC is in "GT Mode"...and I'm off grid. I have doubled checked everywhere in the Mate, Inverter, CC and FNDC for settings relating to Grid Tied and made sure they were set properly, and they are now however, CC still showing "...
by raysun
Wed May 18, 2022 9:08 am
Forum: RADIAN Series
Topic: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK
Replies: 8
Views: 381

Re: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK

If the math is easy, why is it wrong in the original post? The stated design goal was a 10000AH battery. Obviously impossible with 5 200AH monoblocs. When a 60V battery was configured did the inverter start? Nowhere in the GS8048 documentation that I could find does it state the inverter charger sup...
by raysun
Tue May 17, 2022 3:39 pm
Forum: RADIAN Series
Topic: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK
Replies: 8
Views: 381

Re: Using 5x 12volt batteries for 60V.. CC-OK Inverter-NOK

I was using 4x12 200Ah AGM Batteris in the "48Volt" configuration and wanted to add a another battery to make the battery pack 10000Ah. now the flex charge controller has not problem with the absorb voltage of 73.5 or the float of 68.5V. but the Mate3a for the inverter GS8048a will not go...
by raysun
Tue May 17, 2022 10:05 am
Forum: OutBack
Topic: Technical/Service Provider List?
Replies: 1
Views: 658

Re: Technical/Service Provider List?

I wish you good luck in finding a servicing vendor. If its like our area, and most areas I suspect, companies only service what they install. The general reasoning is having no input into the design and installation, vendors have no control over what they would be getting into. Also, service calls t...
by raysun
Tue May 17, 2022 8:56 am
Forum: Website & Forum
Topic: Optics Re Down?
Replies: 1
Views: 91

Re: Optics Re Down?

Everybody else. OB is working on it.
by raysun
Mon May 16, 2022 8:01 pm
Forum: FLEXware
Topic: Change to 3 phase
Replies: 12
Views: 358

Re: Change to 3 phase

I would trust the string sizing tool. The person doing the code for that knows what they are doing and purposefully allows the limits, but I understand if you are concerned about it. Maximum power or maximum DC/AC ratio can be important, but most important is the Max Isc (in the manual) and Voltage...